Re: New Inverter XW Pro & New Conext Gateway with easy remote monitoring on Conext Insight 2
Just finished a remote configuration of a system in the USVI. The function works well. In the pix below I marked out the code but it should be in the gateway user manual. (I can email it). Once you e…1 · -
Re: MPPT 80-600 Schneider CC shuts off mid day
Your harvest is dropping when you go to float. Do you have any days where this is intermittent. Just from the above screens it looks like configuration is not right. That said if you have history ear…1 · -
Re: MPPT 80-600 Schneider CC shuts off mid day
Yes Thanks Bill ;) Keeping your hands well washed up there ;) ;) Yea send me the damaged one, I will recycle it for you :) You can email me below and I will tell you where to ship it :open_mouth: A D…1 · -
Re: MPPT 80-600 Schneider CC shuts off mid day
AC coupling looks like it is not enabled from your screens. Sometimes a grid glitch or nearby lightning can cause s setting to be corrupted. You have surge protection on DC and AC circuits for the ho…2 · -
Re: MPPT 80-600 Schneider CC shuts off mid day
Sounds reasonable. So you are sure that the array does not matter? Either array will cause only the replacement cc to stop selling randomly, while the other cc sells or charges? What are the DC batte…1 ·